Working on fire engine AC (again)

Friendly format provided to inquire about automotive a/c systems.
Archived Forum

Moderators: bohica2xo, Tim, JohnHere

User avatar
bohica2xo
Preferred Member
Posts: 1170
Read the full article
Joined: Wed May 11, 2016 4:12 pm
Location: Las Vegas, NV

Re: Working on fire engine AC (again)

Post by bohica2xo »

The compressor on that truck easily makes 15,000 btu/h by 3000 compressor shaft RPM. It is a 323 cc/rev unit.

That valve is for a 1978-85 Porsche 928. An R12 car with a little Nippondenso 6E171 compressor. That valve also crosses to Dodge K car, Renault LeCar Dodge mini vans... Nothing with big systems.


Can that valve be installed backwards? or is the liquid line thread different on the in & out?
Dgreen
Posts: 110
Joined: Thu Jun 16, 2016 4:08 am

Re: Working on fire engine AC (again)

Post by Dgreen »

Valve can only go one way.

Friend at the parts store sent this.
Attachments
E070CA3D-65CC-44E9-BC3D-181C8D31B1DE.jpeg
E070CA3D-65CC-44E9-BC3D-181C8D31B1DE.jpeg (37.96 KiB) Viewed 9288 times
Dgreen
Posts: 110
Joined: Thu Jun 16, 2016 4:08 am

Re: Working on fire engine AC (again)

Post by Dgreen »

I have a little more info to add to this puzzle. About a year ago we put on a new compressor. I found the expansion block that got changed when the compressor got changed. It has a Parker number on it. 329-412 It also has R-134A printed on the block. I compared it to a Four Seasons expansion block like what is currently installed on the truck. The hole where the refrigerant enters the block is larger on the one with the Parker number. The Four Seasons doesn’t say R-134A on it.

Is this possibly the reason for the poor cooling and low suction pressure?
Attachments
BE849C1E-F94E-41A2-8D8C-0CB0DB06E82B.jpeg
BE849C1E-F94E-41A2-8D8C-0CB0DB06E82B.jpeg (36.44 KiB) Viewed 9271 times
User avatar
bohica2xo
Preferred Member
Posts: 1170
Joined: Wed May 11, 2016 4:12 pm
Location: Las Vegas, NV

Re: Working on fire engine AC (again)

Post by bohica2xo »

There it is. The wrong TXV.

The CV on the parker valve is about twice that of the 4 seasons replacement.

Twice as much refrigerant mass per minute in to the evaporator.
Dgreen
Posts: 110
Joined: Thu Jun 16, 2016 4:08 am

Re: Working on fire engine AC (again)

Post by Dgreen »

I looked up both expansion block part numbers on the internet. Both say for R-12 and R-134a. I adjusted the valve today and no change. The low side was 11 psi and vent temp 50. The outlet pipe of the evaporator was frosting up.
Attachments
A205596B-6329-4376-82CC-B67B60C3FE61.jpeg
A205596B-6329-4376-82CC-B67B60C3FE61.jpeg (49.04 KiB) Viewed 9249 times
Dgreen
Posts: 110
Joined: Thu Jun 16, 2016 4:08 am

Re: Working on fire engine AC (again)

Post by Dgreen »

I found some info on stationary hvac with expansion valves and the problems caused by too much oil. I’m wondering now it that isn’t the reason for the unsatisfactory cooling we’re getting in our engine? I think it still has too much oil.

Also, the compressor clutch self destructed again last week. New clutch arrived today from AC Kits. Going to remove more oil when we change the clutch.
User avatar
bohica2xo
Preferred Member
Posts: 1170
Joined: Wed May 11, 2016 4:12 pm
Location: Las Vegas, NV

Re: Working on fire engine AC (again)

Post by bohica2xo »

Is that compressor still accumulating oil? I thought you had things cleared up with the oil overcharge.

Yes, too much oil hurts cooling.

But a TXV that can't pass enough refrigerant is how you get high suction pressures at the evaporator when there is not much air moving over it.
Dgreen
Posts: 110
Joined: Thu Jun 16, 2016 4:08 am

Re: Working on fire engine AC (again)

Post by Dgreen »

Last time I drained the oil down to where the sight glass was about 3/4 full. My thinking was some oil would settle in the new drier. No oil was added to the new drier before it was installed. After it ran a while, the sight glass was full again. My plan is to recover the charge so I can change the clutch on the workbench. Will drain the oil down to where it’s half way up the sight glass. Should I try to remove excess oil from the drier or can too much oil ruin them?
Dgreen
Posts: 110
Joined: Thu Jun 16, 2016 4:08 am

Re: Working on fire engine AC (again)

Post by Dgreen »

I may also flush the evaporator and condenser a second time. I’m concerned they may be oil logged now.
User avatar
bohica2xo
Preferred Member
Posts: 1170
Joined: Wed May 11, 2016 4:12 pm
Location: Las Vegas, NV

Re: Working on fire engine AC (again)

Post by bohica2xo »

Wow. That thing is seriously over oiled.

I would at least dump the excess oil from the dryer & reset the sump to 1/2 sightglass. Then run it for a few minutes & check the sightglass again.

Do you have the capacity to do a refrigerant flush on the evaporator?