Leak testing with shop air

Post by robmaxfli »

Its an empty R12 system with Mineral Oil and UVDye installed - but I don't have access to Nitrogen - so I'd like to be able to pressurize with normal shop air. I know air 's got moisture in it but I have another Accumulator that I can put on (and ruin) in the process of leak testing. I can put the new Accumulator back on after I find the leak ...
are there any other good reasons not to use compressor air in this situation?
Also, can I add R134 and pressurize it with the shop air.

thanks
User avatar
Tim
Site Admin
Posts: 1104
Joined: Tue Apr 12, 2016 2:19 pm
Location: Scottsdale, Arizona
Contact:

Re: Leak testing with shop air

Post by Tim »

Use some R134a to place pressure in the system, do not run system. No shop air!
------------------------------
Please support ACKITS.com for your Auto A/C Parts and Tool needs.

Help Support the Forum
robmaxfli
Posts: 31
Joined: Fri May 13, 2016 7:07 am

Re: Leak testing with shop air

Post by robmaxfli »

I don't have a sniffer so I was looking to use soap and water. would this method create enough pressure to use S+W?
User avatar
Tim
Site Admin
Posts: 1104
Joined: Tue Apr 12, 2016 2:19 pm
Location: Scottsdale, Arizona
Contact:

Re: Leak testing with shop air

Post by Tim »

robmaxfli wrote:I don't have a sniffer so I was looking to use soap and water. would this method create enough pressure to use S+W?
Depends on the size of the leak.
------------------------------
Please support ACKITS.com for your Auto A/C Parts and Tool needs.

Help Support the Forum
Dougflas
Posts: 379
Joined: Mon Apr 18, 2016 6:10 pm

Re: Leak testing with shop air

Post by Dougflas »

Do not use soap and water. You will get better results using Big Blue or Snoop.